Scaling issue #61
Replies: 3 comments
-
If the output of the CT is in Volts then it does not have a burden resistor and the jumper should be cut. Otherwise, the output is in mA and the jumper should not be cut. This is printed on the front of the CT. For the 013 it's either 1v or 50mA. The calibration for each is different. |
Beta Was this translation helpful? Give feedback.
-
It says 100A/50mA on the CT.
…On Fri, 10 Sep 2021, 10:14 pm John, ***@***.***> wrote:
If the outputnof the CT is in Volts then it does not have a burden
resistor and the jumper should be cut. Otherwise, the outputnis in mA and
the jumper should not be cut. This is printed on the from of the CT. For
the 013 it's either 1v or 50mA. The calibration for each is different.
—
You are receiving this because you authored the thread.
Reply to this email directly, view it on GitHub
<#61 (comment)>,
or unsubscribe
<https://github.com/notifications/unsubscribe-auth/ABWG5C5JLLWC6T464ZK5M4LUBHZB5ANCNFSM5DZGDLPQ>
.
Triage notifications on the go with GitHub Mobile for iOS
<https://apps.apple.com/app/apple-store/id1477376905?ct=notification-email&mt=8&pt=524675>
or Android
<https://play.google.com/store/apps/details?id=com.github.android&referrer=utm_campaign%3Dnotification-email%26utm_medium%3Demail%26utm_source%3Dgithub>.
|
Beta Was this translation helpful? Give feedback.
-
Out of curiosity, what is your clamp meter reading? I think I'm having an issue similar to yours but unsure since I don't see those listed here. My issue with some details is outlined in #169 |
Beta Was this translation helpful? Give feedback.
-
Hi All,
I hope you can assist with the below, I cannot configure my CT's to scale properly see examples below
I adjusted the below CT's gain differently to align with different current as per the YAML code i have pasted below out of ESPhome on home assistant;
CT4 is set at the default value
As I increase the current on the test set (all CT's are on the same test cable) the current does not scale.
Actual figure circled in red (check with clamp meter as well)
Im sure it must be something simple but I am out of ideas
I am using SCT-013 CT's on a 240V single phase system i get 11.56 Volts AC into the board at 244V.
I have seperated the tracks at the bottom of the board as I understand these cts have built in burden, although I am not sure how i could confirm this, or if it would make a difference
Code below, thanks in advance for the assistance.