Sometimes the remote reading of the meter fails, for shorter or longer periods. In such cases the grid company data point is stipulated (not measured). If you log in to "Min side" on https://elhub.no/ you can download the registered data. You will see an indication on each measurement whether any data point is stipulated. Can you check the data point where you see a discrepancy? |
Beta Was this translation helpful? Give feedback.
-
I also have minor discrepancies, but they are all within 0,02kwh so they are pretty negligible and well within the margins in my setup. Yours sound a bit more problematic. My power company (Gudbrandsdals Energi) shows stipulated usage in the app, and so far that has always showed lower peaks than what was measured by the pow-u. |
Beta Was this translation helpful? Give feedback.
-
OK, so your deviations are difficult to explain, could be related to whole-hour datagrams were missed for some reason (reboot of device? I can only speculate). But I can explain the data flow a bit. Firstly - I have not seen published information regarding the communication on the grid operator's network. I assume there is a buffer in the power meter, in case the wireless communication is lost for a shorter or longer period. I have no idea how large such a buffer could be. The data that is pushed on the HAN port is:
The firmware calculates hourly consumption by subtracting current and previous accumulated energy [Wh]. The real-time counter shown on the main page of our firmware is derived by integrating/accumulating time * power from the meter, to get a running estimate. That estimate is then validated/updated when the whole-hour datagram arrives. If one such whole-hour datagram is for some reason not captured by the reader (maybe it rebooted for some reason), the value may be slightly wrong. We do our best to ensure the firmware is stable, so such reboots should not be frequent - but they may still happen. We have also seen that some ESP devices reeboot from time to time (but infrequently) - with identical firmware as an other identical device. We believe that to be some kind of hardware error in them, but so marginal that it is not possible to detect it during our testing (done before shipping Pow-U/K/P1 devices). |
Beta Was this translation helpful? Give feedback.
-
I try to live on the edge when it comes to the 10kW limit (because 5kW is impossible with two EVs that do a fair bit of driving, and 15kW seems a waste), so for a couple of months I've paid more attention to this data.
This month, I've accidentally sent myself over the limit by a hair, annoyingly enough, and I see AMS reader is reporting 10.20, 10.26 and 9.57 as peaks on the 9th, 3rd and 10th respectively. This puts me annoyingly close to not being over.
However, the grid operator has other numbers for these peaks;
The grid operator also lists a peak on the 2nd at 10,652 (the last hour) which the ams reader appears to have completely missed (bringing my month average up to 10,419). I guess there must have been some sort of connectivity issue around midnight - I'm not familiar with the data the reader receives, but does it not also receive a copy of the full reports sent to the grid operator, so that it could maybe retroactively update hourly consumption numbers if these differ?